Replacing a K2 10Gv2 RAID controller

The K2 10Gv2 RAID controller must be connected to the control network to support the operations in this topic.

If the RAID chassis has a single controller (non-redundant), you must take the K2 SAN offline before replacing a failed controller. Refer to procedures in the Instruction Manual for your RAID storage chassis. The remainder of this procedure does not apply to non-redundant systems.

If the RAID chassis has redundant controllers and is properly cabled and configured for a redundant K2 SAN, you can replace a failed controller while media access is underway, as described in this procedure. When a controller detects a fault on its redundant partner controller, the good controller disables the faulty controller automatically. In most cases an error message informs you of the fault and when you check the controller’s status in Storage Utility it reports as disabled.

However, you can also manually disable a controller. In the event that one of the RAID controllers appears operational, but also reports faults through various log files and status indicators, you can choose to disable the controller and replace it. Disabling the controller and removing it in this way avoids interruptions in signal output that can occur if the module fails or if it is simply hot swapped while it is the active controller. When the replacement RAID controller module is installed, it is automatically enabled and becomes the backup controller.

On a RAID chassis with two controllers, if the replacement controller’s firmware is not the same as the firmware on the redundant (currently installed) controller, the firmware on the replacement controller is automatically upgraded or downgraded to match the current system level firmware.
Note: Refer to the Instruction Manual for your RAID storage chassis for procedures on removing and replacing the RAID controller module.
  1. Open the Storage Utility.
  2. Expand the tree view to display the controllers.
  3. Select the controller and check its status, then proceed as follows:
    • If the faulty controller reports as disabled, proceed to the next step in this procedure.
    • If the faulty controller reports as online, right-click the controller icon in the tree view, and select Advanced | Disable Controller 0 or Disable Controller 1, then click OK to continue.
    The Login Information dialog box opens.


  4. If necessary, enable fields and enter username, password, or controller IP address, then click OK. The Disable Controller wizard opens.
  5. At each wizard page, read messages in the center window to follow progress and wait until the green indicator verifies that operations are complete. Then click Next to proceed.
  6. When a "Controller...disabled" message opens, click Yes to confirm and close the wizard. The RAID controller is disabled. You can check controller status in the Storage Utility. You may need to refresh the display.
    Note: If you accidentally disable the wrong controller, you can enable it again by removing it and then replacing it in the chassis.
  7. Remove and replace the disabled RAID controller module. Refer to procedures in the Instruction Manual for your RAID storage chassis.
  8. On inserting the replacement RAID controller, it initializes and is automatically enabled to become the “backup” RAID controller.